Cisco Catalyst Hardware Installation Guid
Grounding the Switch
Step 1 Use a standard Phillips screwdriver or a ratcheting torque screwdriver with a Phillips head to remove the ground screw from the front panel of the switch. Store the ground screw for later use.
Step 2 If your ground wire is insulated, use a wire stripping tool to strip the 10- to 12-gauge ground wire to 0.5 inch (12.7 millimeter [mm]) ± 0.02 inch (0.5 mm) as shown in Figure 3-2.
Step 3 Insert the ground wire into the ring terminal lug, and using a crimping tool, crimp the ring terminal to the wire
Step 4 Slide the ground screw through the ring terminal.
Step 5 Insert the ground screw into the functional ground screw opening on the front panel.
Step 6 Using a ratcheting torque screwdriver, tighten the ground screw and ring terminal lug to the switch front panel to 15 in-lbs. (240 ounce-force inches [ozf-in.]), as shown in Figure 3-4.